Located in Irving, Texas, the facility collapsed on May 2, 2009, during a severe thunderstorm. Twelve people were injured, one seriously.

Based on the national standards for determining loads and for designing structural steel buildings, NIST researchers studying the Cowboys facility found that the May 2 wind load demands on the building’s framework—a series of identical, rib-like steel frames supporting a tensioned fabric covering—were greater than the capacity of the frame to resist those loads.

Assumptions and approaches used in the design of the Cowboys facility led to the differences between the values originally calculated for the wind load demand and structural frame capacity compared to those derived by the NIST researchers. For instance, the NIST researchers included internal wind pressure due to the presence of vents and multiple doors in their wind load calculations because they classified the building as “partially enclosed” rather than “fully enclosed” as stated in the design documents. The NIST researchers also determined that the building’s fabric could not be relied upon to provide lateral bracing (additional perpendicular support) to the frames in contrast to what was stated in the design documents and that the expected wind resistance of the structure did not account for bending effects in some members of the frame.

The NIST report recommends that such evaluations determine whether or not: (1) the fabric covering provides lateral bracing for structural frames considering its potential for tearing; (2) the building should be considered partially enclosed or fully enclosed based on the openings that may be present around the building’s perimeter; and (3) the failure of one or a few frame members may propagate, leading to a partial or total collapse of the structure.

NIST worked with the National Oceanic and Atmospheric Administration’s (NOAA) National Severe Storms Laboratory to estimate the wind conditions at the time of collapse. The researchers determined that, at the time of collapse, the wind was blowing predominantly from west to east, perpendicular to the long side of the building. Maximum wind speed gusts at the time of collapse were estimated to be in the range of 55 to 65 miles per hour—well below the design wind speed of 90 miles per hour in the national standard for wind loads. The center of a microburst (a small, intense downdraft which results in a localized area of strong winds) associated with the May 2 thunderstorm was located about one mile southwest of the structure at the time of collapse.

According to the NIST and NOAA researchers, the wind field in the vicinity of the Cowboys facility at the time of collapse was consistent with design standards and not unusual. Based on their study of the wind conditions at the time of collapse and the structural response, the NIST researchers determined the following likely collapse sequence:

• Buckling of the inner chord (inner side of the roof truss) of a frame in a section of the roof on the east side resulted in the formation of a kink in the frame.

• Failures of the east and west “knees” (connections between the side walls and the roof) allowed the frame to sway eastward with the wind.

• Compressive failure of the east side at the roof’s highest point (ridge) led to fractures of the nearby inner and outer chords in the vicinity of the ridge.

• A progression of frame failures throughout the structure resulted in total structural collapse.

The draft report is available online HERE
Slide Presentation HERE

Tags: collapse, failure, nist, rescue, weather

Share/Send to Friends & Co-Workers

Reply to This

Sign in

E-mail

Password
 or Sign Up
By signing in, you agree to the amended Terms of Service and Privacy Policy.
Forgotten your password?

Latest Nation Member Activity

At least you can use lights. Where I'm from State Law & most insurance's prohibit POV's from running lights until the vehicle is stationary. Even though it would be really scary to see some of the volunteer firefighter's around here allowed to run...
1 minute ago
Jeff Wackerman added 3 photos
4 minutes ago
I don't think that fits me anymore
6 minutes ago
Wow - reading that article I'm thinking - "Is this New York State they're talking about?" I have to disagree - the first problem is getting people to join up. In many VFDs here that's as easy as filling out an application and paying dues. New mem...
8 minutes ago

FFN eMail Alerts

Get hot content from FFN and FireRescue
FireRescue eNewsletter
Breaking & Daily News
Special Promotions
Webcast/Content Alerts
*Your eMail Address:

© 2009   Created by Firefighter Nation WebChief, an Elsevier Public Safety & Go Forward Media, LLC Product -   Partners: JEMS Connect - FireRescue - JEMS
Contact Us: Report an Issue, Inquire About Advertising & Partnerships
This site is intended for use by current and former fire, rescue & EMS professionals. Non emergency service personnel may be subject to review and removal. Using this site inappropriately to spam/advertise or solicit members in any way will result in account termination. Commercial companies may have profiles, but blogs, forums, videos and photos may not be used for self-promotion.

Badges  |  Contact Firefighter Nation  |  Privacy  |  Terms of Service